User: romex jockey101, Location: Texas
Asked on: Tuesday, January 18, 2011 at 10:11 pm EST
Answered on: Tuesday, May 14, 2024 at 12:26 am EDT
Question: i went into a panel that i was about to run a home run from after looking through the panel i noticed a nuetral wire was burned arouned the insulation very badly. it was a mwbc terminated in a tandem breaker.the circuit was 15 amps and was feeding 2 general lighting circuits in a garage and office.. when i went into the office i noticed a 120 plug heater witch they were using it draws about 12 amps...then i went into the garage and the home owner had a table saw pluged in draws about 13 amps ...bc the tandem breaker only sits on phase a it does not cancel out the unbalanced load and the 14 awg could not handle the load ..so i made shure that one leg was on phase a and and i put the other leg on phase b....this was very dangerous and could of started a fire...mwbc on tandems are very dangerous
Summary
A multi-wire branch circuit (MWBC) terminated in a tandem breaker was overloaded and had a burned neutral wire. The unbalanced load caused by a space heater and a table saw exceeded the capacity of the 14 AWG wire.
Causes
Overloading
The combined load of the space heater (12 amps) and the table saw (13 amps) exceeded the 15 amp rating of the circuit.
Unbalanced Load
Because the tandem breaker sits on only one phase, it did not cancel out the unbalanced load between the two phases.
Insufficient Wire Size
The 14 AWG wire was not sufficient to handle the combined load on both legs.
Consequences
Burned Neutral Wire
The excessive current caused the neutral wire to overheat and burn its insulation.
Fire Hazard
The burned neutral wire could have caused a short circuit and started a fire.
Resolution
To resolve the issue, the load should be balanced by dividing it between the two phases. In this case, one leg was put on phase A and the other on phase B.
Dangers of MWBCs on Tandem Breakers
Increased Risk of Overloading
Tandem breakers do not trip when one leg is overloaded, increasing the risk of wire overheating.
Unbalanced Loads
Tandem breakers do not cancel out unbalanced loads, which can cause excessive currents on one phase and underutilization on the other.
Unsafe Wiring Practices
MWBCs on tandem breakers may lead to wiring practices that violate electrical codes, such as connecting two separate circuits to a single tandem breaker.
Recommendations
Avoid MWBCs on Tandem Breakers
Use separate circuit breakers for each circuit to prevent overloading and unbalanced loads.
Use Proper Wire Size
Select wire that is appropriate for the load requirements of the circuit.
Balance Loads
Divide the load evenly between the two phases to avoid overloading one leg.
Regularly Inspect Wiring: Periodically check electrical panels and wiring for signs of overloading or damage. Flag for review