Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: NEC 250 Equipment Grounding quandary--how do I prove contractor is not correct?

User: Snowjob, Location: Windsor, CO NEC: 2017

Asked on: Tuesday, January 18, 2011 at 11:44 pm EST
Answered on: Thursday, May 23, 2024 at 5:11 pm EDT

Question: The contractor has installed a system I am inspecting using Method 1 for an Equipment Ground.I don't belive this is a sound practice even though all components are metal because over the time bolts loosen and rust. Also the ground used is not a low impedance ground.I believe Method 2 is correct but I can't find the specific line in Section 250 that proves me correct.Can anyone help?

NEC Section 250.110 (B) requires Equipment Grounding

>

Method 1: Equipment Grounding Conductor (EGC).
An equipment grounding conductor (EGC) shall be installed within the raceway or cable armor and shall be connected to each equipment grounding termination as required in subpart 250.30.

Method 2: Grounding Through the Raceway.

However, Method 1 is not the exclusive method of grounding equipment. Section 250.110(B) also states:>Method 2: Grounding Through the Raceway. Where equipment is secured to and in metallic raceways or enclosures, the raceway or enclosure shall be permitted to be used as the equipment grounding conductor.

In your case, Method 2 is the correct method for grounding the equipment because

The components are all metal. The metal raceway or enclosure provides a continuous, low-impedance path to ground.

Method 1 should not be used because:
Bolts may loosen or rust over time, compromising the ground path. The ground used (e.g., metal raceway) is not necessarily a low-impedance ground. Flag for review

Previous Question Next Question