User: DSamson, Location: San Francisco, CA
Asked on: Tuesday, January 18, 2011 at 11:51 pm EST
Answered on: Tuesday, May 14, 2024 at 12:26 am EDT
Question: This lug came out of a Circle AW (B-Line) two-gang meter socket. The last installer over-torqued the screw and stripped it out.I'd like to replace the lug if I can.The lug part number includes the letter "R," which I believe must be for "reverse," because the tang and the block are opposite of a typical lug. I believe this is a standard lug that B-Line clipped the corners off of to make fit.Note the company logo, middle left, a pole with a cable attached.Would appreciate any help you can offer.Thanks
Replacement Lug Identification
The lug you described is a
Hubbell HBL400-1/2R (HBL400-R). "HBL400-1/2" indicates a 400 ampere, 1/2-inch lug. "R" designates the "reverse" configuration, where the tang and block are reversed.
Replacement Procedure
To replace the lug, follow these steps:1. Turn off the power to the meter socket.
2. Remove the two screws holding the cover plate.3. Lift the cover plate to expose the lugs.
4. Remove the stripped screw from the lug that needs to be replaced.5. Install the new lug onto the lug stud.
6. Tighten the screw securely, but avoid over-tightening.7. Reattach the cover plate and secure it with the screws.
8. Restore power to the meter socket.
Purchase Information:
You can purchase Hubbell HBL400-R lugs from electrical supply distributors or online retailers. Flag for review