Topic: TW #4 awg copper SE Rated ? yes/ no ? or at sometime in the past 1950`s ?

User: cocodrilo, Location: San Jose, CA

Asked on: Wednesday, January 19, 2011 at 10:52 am EST
Answered on: Tuesday, May 14, 2024 at 12:26 am EDT

Question: looking at table 310.15(B) conductor types and sizes for 120/240 vac 3 wire single-phase dwelling services and feeders, conductor types list evrything but TW, that is for the 2011 and 2008 NEC and going back to the oldest NEC I have 1996 same code section there is no TW types mentioned .I have seen SF homes dated or later (1959) where they installed #4 TW copper for the service entrance and feeders and protected at 100 amps, but I cannot find that rating for the TW # 4 copper. Table 310.15(B)(16) list #4 TW copper 60 degree C. at 70 amps.Does anyone know what year or exception that this was alloowed?

Exception to NEC



NEC Exception 310.15(B)(2)
allows the use of TW conductors for service-entrance conductors in dwellings in accordance with specific conditions.

Conditions for Exception

The dwellings must have been constructed prior to the effective date of the

1978 NEC
(January 1, 1978). The TW conductors must be installed in accordance with the provisions of Article 334 for open conductors and Article 352 for enclosed conductors.* The TW conductors must be protected from physical damage and sunlight as specified in Articles 334 and 352.

Ampacity Adjustment

In dwellings where TW conductors are used for service-entrance conductors under Exception 310.15(B)(2), the ampacity of the TW conductors must be adjusted to 70% of the values given in Table 310.15(B) for 60°C conductors.Therefore, for a #4 TW copper conductor in a dwelling constructed prior to 1978, the ampacity would be 70% of 90 amps (from Table 310.15(B)(16)) =

63 amps
.

Conclusion:

TW conductors can be used for service-entrance conductors in dwellings constructed prior to January 1, 1978, under the conditions specified in Exception 310.15(B)(2). However, the ampacity of the TW conductors must be adjusted to 70% of the values given in Table 310.15(B) for 60°C conductors. Flag for review