Topic: Bank general lighting & recept load

User: Finite10, Location: Great NW

Asked on: Wednesday, January 19, 2011 at 11:01 am EST
Answered on: Tuesday, May 14, 2024 at 12:27 am EDT

Question: From Mike's Master/Contractor Simulated Exam: part 3 q. 27What's the general lighting and receptacle load for a 30,000 sq ft bank?The answer key says to multiply the lighting load of 3.5VA/sq ft from the table by 1.25.I got 135KVA but that's not one of the answer choices.I thought Table 220.12 load was THE load. The question does not ask for feeder conductor size discussed in 215.2(A), or OCPD or Service for that matter.

The general lighting and receptacle load for a 30,000 sq ft bank is 120 kVA.To calculate this, you multiply the lighting load of 3.5 VA/sq ft from Table 220.12 by 1.
25.So, 3.5 VA/sq ft x 30,000 sq ft = 105,000 VA105,000 VA x 1.25 = 120 kVAThe answer key is incorrect. 135 kVA is not one of the answer choices because it is not the correct answer. Flag for review