User: sparkymarjon, Location: Tennessee
Asked on: Wednesday, January 19, 2011 at 11:36 am EST
Answered on: Tuesday, May 14, 2024 at 12:27 am EDT
Question: A debate came up so I thought I would bring it here, If you have, let's say 6- 2wire s.p. circuits in a conduit do you count the nuetrals for derating purposes. I feel because you have multiple different circuits in the same conduit, yes. However others feel that since they are all 2 wire circuits and the nuetral is carrying back the balance load of the hot leg,they cancel each other out and have no effect on the other conductors. I feel since there are amps in both nuetral and hot leg, there will be a heating effect when mixed with other conductors, which is why you need to count nuetrals for derating.. how do you feel
According to the National Electrical Code (NEC), neutral conductors are counted for derating purposes in conduits containing multiple circuits.Reasoning
Neutral conductors carry return current. While the neutral and hot legs of a circuit may carry equal and opposite currents under balanced loads, there can be imbalances in real-world situations. These imbalances can cause the neutral conductor to carry significant current, resulting in heating and potential insulation damage. Conduit fill calculations consider all conductors. NEC Table 310.15(B)(3)(a) requires all conductors, including neutrals, to be counted when calculating conduit fill. This ensures that the conduit is not overcrowded, which could lead to insufficient heat dissipation. Multiple circuits in a conduit. When multiple circuits are run in the same conduit, the heating effect of all conductors accumulates. Counting neutrals ensures that the total ampacity is not exceeded, preventing overheating and potential hazards.
Example
Consider a conduit with six 2-wire circuits, each rated for 15 amps.
Without neutral derating
The conduit fill would be 6 x 2 = 12 conductors.*
With neutral derating
The conduit fill would be 6 x 2 + 6 = 18 conductors (6 hot conductors + 6 neutral conductors).Since the conduit fill exceeds the allowable fill percentage for the given conduit size, neutral derating would be necessary to ensure compliance with the NEC.
Conclusion:
Counting neutrals for derating purposes in conduits containing multiple circuits is essential to ensure proper heat dissipation, prevent overheating, and comply with the NEC requirements. Flag for review