Question: Hi everyone,I'm the electrical designer for a T/I which calls for new rooftop units...I found a few threads with similar multi-motor situations...And wanted to make sure I'm on the same page.I'd like to know if I am correctly sizing a feeder to feed an rooftop AC unit and supply fan. Voltage is at 460V 3-phase.The AC unit is a 5-Ton AAON that states FLA 13A, MCA 15A, MOCP 20AThe supply fan is a 1HP fan with FLA 2.1 per NEC.So to properly size the feeder: 13 + 2.1 = 15.1AThe breaker feeding the two units would be 175% of 15.1 so 1.75x15.1=26.4 or a 25A breaker.I intend to put a fused disconnect with 20A fuses for the AC and a fused disconnect with 3A fuses for the fan.There are 3 of these going on top of an existing 1975 single-story wood construction building.Thanks much!
Your calculations seem to be correct. Here's a summary of the sizing and protection requirements
Feeder Sizing:
Total load current: 13A (AC unit) + 2.1A (fan) = 15.1A Feeder ampacity: 1.75 x 15.1A = 26.4A Feeder size: #10 AWG THHN (copper)Breaker Sizing
Breaker size: 25A (next standard size above 26.4A)
Fused Disconnect Sizing
AC unit fused disconnect: 20A fuses Fan fused disconnect: 3A fuses
Note
The MOCP (Maximum Overload Current Protection) of 20A for the AC unit should be used when selecting the feeder ampacity. The National Electrical Code (NEC) requires a 150% multiplier for branch circuit conductors supplying motor loads. The fused disconnects provide additional protection for the AC unit and fan in case of a fault.
Additional Considerations: Verify the voltage rating of the rooftop units and supply fan matches the 460V supply. Ensure that the feeder cable is properly sized for the voltage, current, and distance to the rooftop units. Install appropriate conduit, fittings, and supports for the feeder cable.* Follow all applicable electrical codes and standards. Flag for review