Question: Hello,This is my first posting in this site.I have a 45KW generator that can produce 156Amps for 120/208V (which is the current service) . The loads that I want to back up is as follow:150 Amps at 208V and 56 Amps at 120v.Obviously this generator does not has the capability to supply both loads. These loads are from 2 freezers and 4 refrigerators. It seems odd that an 45kw cannot provide power to these number of appliances is this correct?The way I calculated the loads is by adding the face plate values (FLC). Do I missing something?
Yes, it seems odd that a 45 kW generator cannot provide power to 150 Amps at 208V and 56 Amps at 120V. Let's check your calculations and see if we can identify any errors.
Total Load
Total load = 150 Amps 208V + 56 Amps 120VTotal load = 31,200 VA + 6,720 VATotal load = 37,920 VA
Generator Capacity
Generator capacity = 45 kWGenerator capacity = 45,000 VA
Comparison
Total load = 37,920 VAGenerator capacity = 45,000 VAAs you can see, the generator capacity is indeed sufficient to handle the total load.
Possible Explanations
Faulty Generator
The generator may not be operating at its full capacity or there could be a technical issue limiting its output.
Incorrect Load Calculations
You mentioned that you used the face plate values (FLC) to calculate the loads. While this is a reasonable estimate, it doesn't account for factors like surge currents or power factor. Surges during startup can temporarily exceed the FLC, and power factor can reduce the actual power drawn.
Other Loads Connected
Are there any other loads connected to the generator that you may not have accounted for? Even small loads can add up and affect the generator's capacity.
Recommendations
Test the Generator
Verify the generator's output using a load bank or test equipment to ensure it is operating properly.
Recalculate Loads
Use a more accurate method for calculating the loads, considering factors like surge currents and power factor.
Check for Additional Loads: Ensure that there are no hidden loads connected to the generator that you are unaware of.If you have confirmed that your calculations are accurate and the generator is functioning properly, then it is possible that the generator may have specific limitations or requirements for these particular appliances. Consult the generator's specifications or contact the manufacturer for more information. Flag for review