User: curley7714, Location: NC & IN
Asked on: Wednesday, January 19, 2011 at 2:23 pm EST
Answered on: Tuesday, May 14, 2024 at 12:27 am EDT
Question: Is it code compliant to splice wires in a cellular floor raceway where accessible?
NEC 2020, Article 300.15(A)(2) - Splices in Underfloor Raceways and Cellular Floor Raceways.Splices or taps shall be made only in junction boxes, except as permitted in 300.15(A)(2)(a) through (A)(2)(d).(a) In cellular concrete floor raceways, taps or splices shall be made only in access boxes installed at the time of the original installation.(b) In other types of underfloor raceways, taps or splices shall be made only in metal junction boxes installed at the time of the original installation.(c) Taps or splices made in metal junction boxes shall have a cover that is screw fastened or secured by substantial snap catches.(d) In cellular floors, splices or taps may be made between outlets where the splice is accessible without damage to the building structure. Flag for review