User: pqtest, Location: Charlotte, NC
Asked on: Wednesday, January 19, 2011 at 3:15 pm EST
Answered on: Tuesday, May 14, 2024 at 12:27 am EDT
Question: Hello all,It has been a while since I last posted. We are working on a contract that requires our techs to wear 8cal FR clothing. I want to purchase new, but someone at our company has identified a source that has literally pallets of used FR clothing. I really don't want to sort through this mess looking for what is good and what is bad, and then trying to guess everybody's correct size. If it had been washed, folded, sized and properly maintained, it might be a good idea. However, it is just in a giant mound of shirts, pants and jackets sitting in a warehouse.My question is, can anyone give me a reference from 70E or OSHA that talks about used FR clothing? Frankly, I am trying to justify my position to purchase new. I think I can make a case using NFPA70E Article 130.7(16) which discusses proper storage of clothing, but I want to hit this thing with the biggest hammer I can just to kill the issue.I thought I had seen something years ago from OSHA that prohibited issuing used safety equipment to an individual worker for their exclusive use, but cannot find that information now.Thanks!
NFPA 70E Article 130.7(16): "FR clothing shall be stored in a clean, dry location, protected from sunlight, heat, chemicals, and other elements that may damage the clothing."OSHA Regulations 29 CFR 1910.132(a) requires employers to provide personal protective equipment (PPE) that is "in good condition." 29 CFR 1910.138(a)(2) requires electrical workers to use FR clothing "that is designed and used in accordance with the requirements of NFPA 70E." 29 CFR 1910.156(e)(2) requires employers to conduct inspections of PPE on a regular basis to ensure its continued effectiveness.
Interpretation
These regulations and standards suggest that: Used FR clothing may not meet the requirements of NFPA 70E and OSHA if it has not been properly stored and maintained. Employers are responsible for ensuring that PPE is in good condition and meets applicable standards.* Issuing used FR clothing that has not been inspected and verified to meet requirements could expose employees to hazards.
Conclusion
Based on the references provided, there is a strong case to be made for purchasing new FR clothing rather than using used clothing that has not been properly stored and maintained. Used FR clothing may not meet industry standards and could compromise worker safety. Flag for review