Question: Hello guys and gals.The 2011 NEC definition of system bonding jumper is:"the connection between the grounded circuit conductor and the supply side bonding jumper, or the equipment grounding conductor, or both, at a separately derived system"What is meant by the supply side bonding jumper? Are they talking about the main bonding jumper of the service and/or the system bonding jumper of the separately derived system supplying the separately derived sytem?Thanks for all replies.
The supply side bonding jumper is the bonding jumper that connects the grounded circuit conductor (neutral) of the supply system to the equipment grounding conductor (green wire) at the service entrance.This bonding jumper ensures that the grounded circuit conductor and the equipment grounding conductor are at the same potential, which helps to prevent electrical shock. Flag for review