Question: Commercial setting: gas powered water heater in secure enclosed room.120volt cord & plug striker for pilot light.120v/15a standard duplex in metal "Bell" box fed via 12-2 w/ground mc to standard single pole 120v/15a toggle switch in 4 square box w/ RS cover. Then 1/2" emt to panel (located elsewhere), with no compression fittings. Existing conditions except the new furnace and striker replacements.What is right and wrong with this whole picture? Also, being existing conditions can this be plugged back in or does it need hard wiring with disconnect? Jurisdiction is Collier County, FL under '08 adopted code.Please advise include NEC, FL building, Fire, Handbook references. Thank you!
What's Right
Gas water heater in a secure enclosed room 120V cord and plug for pilot light
What's Wrong
1. Wiring for Pilot Light
The 120V/15A standard duplex outlet in the metal "Bell" box should not be used to power the pilot light. Refer to NEC 422.16(B)(3) for the proper type of receptacle and configuration for gas appliance ignition.
2. Wiring to Panel
The use of 1/2" EMT without compression fittings violates NEC 250.106(A).
3. Switch and Cover Plate
A single-pole toggle switch in a 4 square box with an RS cover is not appropriate for this application. Refer to NEC 404.2 for proper switch and cover plate requirements.
Existing Conditions
As per the NEC, the existing conditions are not compliant with current code requirements.
Replugging In
No, the water heater should not be plugged back into the existing outlet. Hardwiring with a disconnect is required.
Code References
NEC 422.16(B)(3) - Receptacles for Appliance Ignition NEC 250.106(A) - Compression Fittings NEC 404.2 - Switches and Receptacles
Florida Building, Fire, and Handbook References: Florida Building Code (FBC) - Section 626.2 - Gas-Fired Appliances Florida Fire Prevention Code (FFPC) - Chapter 23 - Liquefied Petroleum Gas* Florida Handbook of Electrical Inspection - Chapter 8 - Special Equipment Flag for review