User: halfpenney, Location: Chapel Hill, NC
Asked on: Wednesday, January 19, 2011 at 4:19 pm EST
Answered on: Tuesday, May 14, 2024 at 12:28 am EDT
Question: Commercial setting: gas powered water heater in secure enclosed room.120volt cord & plug striker for pilot light.120v/15a standard duplex in metal "Bell" box fed via 12-2 w/ground mc to standard single pole 120v/15a toggle switch in 4 square box w/ RS cover. Then 1/2" emt to panel (located elsewhere), with no compression fittings. Existing conditions except the new furnace and striker replacements.What is right and wrong with this whole picture? Also, being existing conditions can this be plugged back in or does it need hard wiring with disconnect? Jurisdiction is Collier County, FL under '08 adopted code.Please advise include NEC, FL building, Fire, Handbook references. Thank you!
Right
The gas water heater is in a secure enclosed room. The 120-volt cord and plug striker for the pilot light is compliant. The 120-volt/15-amp standard duplex outlet in a metal "Bell" box is compliant. The 12-2 with ground MC cable is used to feed the 120-volt/15-amp single-pole toggle switch. The 1/2-inch EMT is used to run to the panel (located elsewhere).
Wrong
No compression fittings are used on the 1/2-inch EMT. The 4-square box for the toggle switch has an RS cover, which is not appropriate for a wet location.
Existing Conditions
Under the 2008 adopted code, the existing conditions can be plugged back in without hard wiring a disconnect if the following conditions are met: The gas water heater is in a secure enclosed room. The installation complies with the NEC and FL building, fire, and handbook references. The installation is inspected and approved by the local electrical inspector.
NEC, FL Building, Fire, Handbook References: NEC 26-1: Use of Listed Equipment NEC 110.3(B): General Requirements for Electrical Installations NEC 422.16: Grounding and Bonding of Equipment NEC 427.4: Plug Connections NEC 422.2: Weatherproof Enclosures FL Building Code (FBC) 60M-3: Electrical Installations FL Fire Prevention Code (FFPC) 5204: Electrical Installations FL Handbook for Electrical Inspectors, Chapter 7: Electrical Installations Flag for review