Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounding and bonding at the service

User: wmeek, Location: Texas

Asked on: Wednesday, January 19, 2011 at 5:45 pm EST
Answered on: Tuesday, May 14, 2024 at 12:28 am EDT

Question: I have a 320 Meter can and PoCo requires a ground in the metercan to a ground rod. I was going to run all other GEC conductors to the supply side gutter and terminate them using a Ground bar per 250.64(F) My questions , an i am confused. If you run a #6 conductor to the grounding electrode( ground rod) at the meter can and then you ran the neutrals from the metercan to each service disconnect ,wouldn't you be bonding the neutral in two different locations. This is just puzzling me.Thanks

Bonding vs. Grounding Bonding connects conductors together, typically to ensure that they are at the same electrical potential. Grounding connects a conductor or equipment to the earth to dissipate electrical energy.

Grounding at the Meter Can The ground rod at the meter can provides a grounding point for the electrical system. The #6 conductor from the meter can to the ground rod is the grounding electrode conductor (GEC). The GEC connects the electrical system to the earth and provides a path for fault currents to the ground.

Neutral Conductor
The neutral conductor carries the unbalanced current in a single-phase system and the return current in a three-phase system. The neutral conductor is typically grounded at the transformer or at the service entrance panel, but it can also be grounded at other locations.

Bonding the Neutral
The neutral conductor is bonded to the GEC at the service entrance to ensure that the neutral system is at the same potential as the grounding system. This bonding point is typically located at the main panel or where the feeder enters the building.

Separation of Grounding and Neutral
Article 250.64(F) requires that the grounding system and the neutral system be kept separate from each other except at the service entrance or where otherwise permitted.* This means that the neutral conductor should not be connected to the grounding system at multiple locations.

Your Situation

If you run neutrals from the meter can to each service disconnect and also bond the neutral to the GEC at the meter can, you will be bonding the neutral in two different locations. This is not permitted by code and would defeat the purpose of maintaining the separation of the grounding and neutral systems.

Correct Approach

The correct approach is to:1. Bond the neutral to the GEC at the service entrance.
2. Run the #6 GEC from the meter can to the ground rod.3. Run all other GEC conductors from the meter can to the supply side gutter and terminate them using a ground bar per 250.64(F). Flag for review

Previous Question Next Question