User: RCRosson, Location: Thousand Oaks, CA
Asked on: Wednesday, January 19, 2011 at 7:26 pm EST
Answered on: Tuesday, May 14, 2024 at 12:28 am EDT
Question: Hello,I'm working a job in Downtown Los Angeles area and the inspector hit me for not having a HOT water bond. I'm familar with inspectors calling for the gas to cold water, which I did at the water heater; then in a continious run, ran to the new 100 amp meter main service. I ran an additional bond straight to the new ground rod just below the panel. Doesn't the fact that the plumbing is tied together at the facets eliminate the need for a redundant bond to the hot water?Thanks.
The answer is no.The inspector is correct in requiring a hot water bond.The gas to cold water bond and the ground rod bond are not redundant with the hot water bond.The gas to cold water bond is intended to equalize the electrical potential between the gas and water systems, which can help to prevent corrosion.The ground rod bond is intended to provide a low-resistance path to ground for electrical faults, which can help to protect people and property from electrical shock.The hot water bond is intended to equalize the electrical potential between the hot and cold water systems, which can help to prevent corrosion and electrical shock.In your case, even though the plumbing is tied together at the faucets, there is still a potential for a difference in electrical potential between the hot and cold water systems. This is because the hot water heater can introduce electrical current into the hot water system, which can then be transferred to the cold water system through the faucets.The hot water bond helps to prevent this by providing a low-resistance path for electrical current to flow between the hot and cold water systems, thus equalizing their electrical potential.Therefore, it is important to install a hot water bond in addition to the other bonding requirements. Flag for review