Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Low Voltage Lighting

User: monkey, Location: Arizona

Asked on: Wednesday, January 19, 2011 at 10:05 pm EST
Answered on: Tuesday, May 14, 2024 at 12:29 am EDT

Question: I have never really liked it and have not installed very much. I have been called in to a job where the handyman installed little 2" cans with 35 watt MR-11 lamps. They called because 1 bank quit working. After finally locating the transformers buried in an inaccessable ceiling I found he had extended the leads supplied with the cans with some zip cord, open splices. The only splices in a box (buried of course) were the line side of the txformers. I know it's not safe or legal (the open 12V splices and the zip cord), but I can't find the proper code section to back me up.Any help would be appreciatedBrian

National Electrical Code (NEC)Article 400 - Flexible Cords and Cables 400.8(4) Open splices in flexible cords are prohibited. 400.8(6) Flexible cords shall not be used as a permanent wiring method.

Article 410 - Luminaires (Lighting Fixtures) 410.11 Luminaires shall be installed and equipped in accordance with any instructions included in the listing or labeling. 410.13(A) All wiring shall be done in accordance with Article 300 - Wiring Methods and Materials.

Article 300 - Wiring Methods and Materials 300.14(A) Conductors shall not be spliced outside junction boxes, device boxes, or conduit bodies, unless specifically permitted elsewhere in the Code.

Additional Information
The use of zip cord for permanent wiring is not permitted, as it is not suitable for concealed wiring and is not rated for the voltage and current involved. The extension of the leads supplied with the cans using zip cord is a violation of the listing requirements for the cans, as the leads are not intended to be extended. The buried transformers and splices create a safety hazard, as they are not accessible for inspection or maintenance.

Conclusion

Based on the NEC sections listed above, the open 12V splices and the use of zip cord in this installation are both unsafe and non-compliant with the Code. Flag for review

Previous Question Next Question