Topic: Is Genral Lighting Load taken at continuous 125%?

User: Finite10, Location: Great NW

Asked on: Thursday, January 20, 2011 at 9:21 am EST
Answered on: Tuesday, May 14, 2024 at 12:29 am EDT

Question: Al my exam prep calculations say to take lighting at 125% when it's continuous, as in a commercial building, but I can't find it anywhere in article 220 Load Calculations.I thought Table 220.12 load minus Table 220.42 Demand Factor was THE minimum lighting load.The exam prep questions do not ask for:1) feeder conductor size discussed in 215.2(A)2) OCPD3) ServicerWhere loads are taken at 125% when continuous.What is the code citation I am missing?

Article 220.42 provides a demand factor for lighting loads in commercial and industrial buildings. This demand factor is not applicable to continuous lighting loads, such as in a commercial building.However, the National Electrical Code (NEC) does not specifically require that continuous lighting loads be calculated at 125% of their actual load. This requirement is typically found in local building codes or industry standards.For example, the California Building Code (CBC) requires that continuous lighting loads be calculated at 125% of their actual load. This requirement is found in Section C305.3(A) of the CBC.Therefore, if you are taking an exam that is based on the California Building Code, you would be correct in taking lighting loads at 125% when they are continuous. However, if you are taking an exam that is based on the NEC, you would not be required to do this.It is important to note that local building codes and industry standards can vary from the NEC. Therefore, it is always important to check the applicable codes and standards for your specific project. Flag for review

Previous Question Next Question