Question: If a motor is protected by a circuit breaker, does the local non fused disconnecting means need to have an ampacity rating equal or larger than the circuit breaker? If not, what code reference covers this?
Yes, the local non-fused disconnecting means must have an ampacity rating equal to or larger than the circuit breaker. This is covered by NEC 430.110(A) and 430.