Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Local Motor Disconnect Size

User: Artemis, Location: Logan, Utah

Asked on: Thursday, January 20, 2011 at 3:06 pm EST
Answered on: Tuesday, May 14, 2024 at 12:30 am EDT

Question: If a motor is protected by a circuit breaker, does the local non fused disconnecting means need to have an ampacity rating equal or larger than the circuit breaker? If not, what code reference covers this?

Yes, the local non-fused disconnecting means must have an ampacity rating equal to or larger than the circuit breaker. This is covered by NEC 430.110(A) and 430.
113. Flag for review

Previous Question Next Question