User: AmazingTrans, Location: Australia
Asked on: Thursday, January 20, 2011 at 3:45 pm EST
Answered on: Tuesday, May 14, 2024 at 12:30 am EDT
Question: Hi everybody,I'm have a couple of questions which i am not sure in accord to CUL & NEC standard on sizing a 1.5HP motor that runs at 460V @ 2.4 FLA. It is use for an oil pump which a lot of times it starts and stops, and mostly run continuously.1. What size should the Circuit breaker be size at? is it 115% higher, 125%, 150%?2. What type of trip curve should my CB be? C? D?Hope to hear from someone!thanks
1. Circuit Breaker Size
According to the National Electrical Code (NEC) and the Canadian Electrical Code (CEC), the circuit breaker size should be based on the motor's full load current (FLA) and the motor's service factor.The motor's full load current is given as 2.4 FLA. The service factor is not provided, so we'll assume a typical service factor of 1.
15.Using the NEC/CEC table 430.52
FLA (2.4) x Service Factor (1.15) x % Overcurrent = Circuit Breaker Size
115% Overcurrent for infrequent starting: 2.4 x 1.15 x 1.15 = 2.99 A 125% Overcurrent for frequent starting: 2.4 x 1.15 x 1.25 = 3.21 A 150% Overcurrent for very frequent starting or heavy starting load: 2.4 x 1.15 x 1.50 = 3.72 A
Based on these calculations, the circuit breaker should be sized at 3.21 A for frequent starting conditions.2. Trip Curve
For a motor application, a Type D trip curve is typically recommended. This curve provides a time delay that allows the motor to start and reach its operating speed without tripping the breaker.
Summary Circuit breaker size: 3.21 A* Trip curve: Type D Flag for review