Question: I have an unbalanced IR Heater load setup as a delta load. Voltage is 3-phase 240VAC. There are multiple heaters in parallel between each pair of phases. We are simply looking for a method to tell how many bad heating elements there are.I can measure the line currents easily, but I believe I need to convert these to phase currents to properly find wattage used between two phases. I can calculate line current magnitudes based on phase currents assuming 120 degrees of separation between phases. But, I cannot figure out how to calculate phase current magnitudes based on line currents. Using a recommendation I read on here from forum member topgone, I created an excel sheet that will use the add-in "solver" to find the phase currents required to match up with our measured RMS line currents.While the excel solver does seem to work, I cannot figure out the equations to do it mathematically. Can anyone help me with a mathematical method to calculate phase currents from measured RMS line currents with an unknown-unbalanced delta load?
Mathematical Method to Calculate Phase Currents from RMS Line CurrentsAssumptions
Balanced delta load (equal impedances in each phase) Unknown unbalanced phase currents Measured RMS line currents
Equations
Let: IA, IB, IC = phase currents IAB, IBC, ICA = RMS line currents
Phase Current Magnitudes|IA| = √((2/3) |IAB|2 - (1/3) (|IBC|2 + |ICA|2))|IB| = √((2/3) |IBC|2 - (1/3) (|ICA|2 + |IAB|2))|IC| = √((2/3) |ICA|2 - (1/3) (|IAB|2 + |IBC|2))
Phase Current AnglesθA = arctan((IAB / 2) √3 / (|IAB|2 - |IBC|2))θB = arctan((IBC / 2) √3 / (|IBC|2 - |ICA|2))θC = arctan((ICA / 2) √3 / (|ICA|2 - |IAB|2))
Example
If the measured RMS line currents are: IAB = 10 A IBC = 12 A ICA = 8 AThen the phase currents are: IA = 7.07 A IB = 8.49 A IC = 5.48 A
Note: The phase currents calculated using this method will be complex numbers. The magnitudes represent the effective (RMS) values of the currents.* The angles represent the phase shifts with respect to the reference phase (usually phase A). Flag for review