Question: The fire suppression system for a commercial kitchen was moved, fire suppression people just left the wiring as is. There is a box containing a single pole switch (this switch according to the owner is able to turn the Exhust Fan on and off),it was wired with, in one conduit the hot and a white wire with orange tape ( this is the switchleg to the exhust fan). In the other conduit that was a black, and a white with orange tape these went to the fire suppression box that has a red, black and yellow leads. I believe the red is the common and the others are a NO and NC lead from a microswitch. I opened the switch box and disconnected what was there to refeed the fire suppression system. Doing so I have forgot how the switch was wired. any ideas? does the hot just feed through the box to the common of the FS system and then the NO lead become the switchleg back to the exhust fan switch? Help please
Original Wiring
Incoming Conduit 1
Hot (black) Switchleg to exhaust fan (white with orange tape)
Incoming Conduit 2
Neutral (white) with orange tape Black wire from fire suppression box (NC contact) White wire from fire suppression box (NO contact)
Fire Suppression Box Wiring
Red Wire
Common
Black Wire (NC Contact)
Normally Closed (connects to Common when not activated)
Yellow Wire (NO Contact)
Normally Open (connects to Common when activated)
Reconnection Procedure
1.
Disconnect all wires from the single pole switch.2. Reinstall the fire suppression system.3. Connect the black wire from the fire suppression box (NC contact) to the incoming neutral wire (white with orange tape).4. Connect the red wire from the fire suppression box (Common) to the incoming hot wire (black).5. Connect the yellow wire from the fire suppression box (NO contact) to the switchleg to the exhaust fan (white with orange tape).Switch Wiring
Hot wire (black) from incoming Conduit 1
Connect to the top terminal of the single pole switch.
Switchleg to exhaust fan (white with orange tape)
Connect to the bottom terminal of the single pole switch.
Operation: When the fire suppression system is not activated, the black wire (NC contact) is connected to the neutral wire, completing the circuit to the exhaust fan switch. When the fire suppression system is activated, the yellow wire (NO contact) is connected to the common wire, completing the circuit to the exhaust fan switch and turning on the exhaust fan. Flag for review