Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: fault in a water filled handhole

User: mshields, Location: Boston, MA

Asked on: Thursday, January 20, 2011 at 6:34 pm EST
Answered on: Tuesday, May 14, 2024 at 12:32 am EDT

Question: Got called out to take a look a look at the aftermath of a fault on a 200A, 480V feeder. The fault occured in a water filled handhole between two phase conductors. None of the three upstream breakers tripped. Instead, the water actually came to a boil and the steam alerted people to a problem.Naturally, the whole run will be replaced. But I'm wondering if the Instantaneous setting on the 200A MCCB, if set to something less than Max (as it was) would have at least cleared the fault.I imagine the only sure way to catch such a fault is with ground fault which in this case was only on the 3000A main upstream and it didn't trip either.Would setting the Instantaneous lower have done anything in this instance? How much current will flow through water. I guess it's a function of the distance so let's say 4 or 5 inches apart? Anybody know?Thanks

Would setting the Instantaneous lower have done anything in this instance?

Possibly. The Instantaneous setting on an MCCB is designed to trip the breaker within a few milliseconds of a fault that exceeds the set value. In this case, the fault current was likely not high enough to trip the MCCB's regular overload protection, but it may have been high enough to trip the Instantaneous setting if it was set lower.

How much current will flow through water?

The amount of current that flows through water depends on several factors, including: Water resistivity

The resistivity of water is a measure of its resistance to the flow of electrical current. Higher resistivity means less current flows, and vice versa.


Distance between conductors

The shorter the distance between conductors, the more current will flow.

Voltage

The higher the voltage, the more current will flow.


Frequency

AC current will flow more easily through water than DC current.In this case, the water resistivity is likely fairly low, the distance between conductors is relatively small, and the voltage is high (480V). Therefore, it is likely that a significant amount of current flowed through the water.

Calculation

Using Ohm's Law (I = V / R), we can estimate the current that flowed through the water:

I = V / R
V = 480V R = ? (unknown)We can estimate the resistance of the water using the following formula:
R = ρL / A
ρ = resistivity of water (20 micro-ohm-cm) L = distance between conductors (5 cm) A = cross-sectional area of water (assuming a cylindrical shape with a diameter of 1 cm)
A = πr² = 3.14  (0.5 cm)² = 0.785 cm²
R = 20 micro-ohm-cm * 5 cm / 0.785 cm² = 127.3 micro-ohms
I = 480V / 127.3 micro-ohms = 3774A
Therefore, it is estimated that over 3000A flowed through the water.


Conclusion:


Setting the Instantaneous setting on the MCCB to a lower value may have tripped the breaker and prevented the fault from escalating. However, it is not certain that the lower setting would have been low enough to trip the breaker for this particular fault, as the current through the water was likely very high.Additionally, installing a ground fault protection device on the feeder could have also helped to detect the fault and trip the breaker. Flag for review

Previous Question Next Question