Question: Does NEC have any requirement for removing abandoned conduit, which does or does not have any wire in the conduit?I'm ask because I'm expecting a debate to come up with an installation. The requirement is to replace an existing fire alarm system with a new system while the old system remains operational.The client doesn't want to pay to remove the old conduit, wire, junction boxes etc. All he wants is to remove the old devices, control panel, and any exposed conduit, which might otherwise look ascetically displeasing. Wires would be rolled back above the ceiling into an old junction box and cover installed, but that's about it.
Abandoned Conduit with Wire
NEC 800.35
Abandoned raceways shall be removed or capped off.
NEC 800.40(B)
If conductors are abandoned in place, they shall be terminated.
Abandoned Conduit without Wire
The NEC does not specifically require the removal of abandoned conduit without wire. However, the following may apply:
NEC 300.16
Raceway installations shall be completed before the conductors are installed.
NEC 300.18
Unused openings in cabinets, boxes, and fittings shall be effectively closed.
Interpretation for Fire Alarm System
In the context of a fire alarm system replacement, it could be argued that the old conduit without wire is effectively "abandoned" since it is no longer serving a purpose in the new system. Therefore, it may be prudent to remove it as per NEC 800.35.Additionally, it is important to consider the following:
NEC 90.5
The purpose of the NEC is to protect persons and property from electrical hazards.
NEC 110.12
Electrical installations shall be safe and not present a hazard to persons or property.Leaving exposed or improperly terminated conduit could potentially create an electrical hazard or interfere with the proper operation of the new fire alarm system. Therefore, it is recommended to at least cap off or seal the abandoned conduit to ensure compliance with NEC 300.18 and to minimize potential risks.
Conclusion:
While there is no explicit NEC requirement to remove abandoned conduit without wire, it is recommended to do so for safety and compliance with NEC principles. In the specific case of a fire alarm system replacement, it is prudent to remove or cap off any abandoned conduit to minimize potential hazards and ensure the proper functionality of the new system. Flag for review