User: DSamson, Location: San Francisco, CA
Asked on: Friday, January 21, 2011 at 1:17 am EST
Answered on: Tuesday, May 14, 2024 at 12:33 am EDT
Question: My wife listens politely, but doesn't really get it.My one year old and three year old don't really have the attention span for it.I trouble shot and fixed my first California 3-way today. I couldn't have done it without this forum.Here's the setup. Two switches at the top of the stairs, two at the bottom of the stairs, controlling 1st floor entry light and light at the top of the stairs, switched independently. Currently operates like someone put a single pole switch at one end. Lights only light when the upstairs switches are in a given position.Owner reports, when they first moved in, 30 YEARS AGO, they would flip the switch and a fuse would blow.I open things up, downstairs switches, three conductors at each switch, one has two connected, one has three connected. They're both 3-way switches.Upstairs switches, 4 conductors total, two to each switch. Both 3-way switches, with one vacant terminal.I take out my meter and my circuit seeker and I figure out:Downstairs, I have, at each switch, a hot a neutral, and a switch leg. Upstairs I have a hot a neutral and two switch legs, one to each light. Thanks to the following post, the rest was easy.don_resqcapt1909-19-03, 03:56 PMHook a hot and a neutral to the terminals where the travelers are normally connected at both 3 ways. Run from one common terminal to one wire at the fixture. Run the other fixture wire to the common on the second 3 way. This circuit siwtches the grounded conductor and also make the lamp socket screw shell hot, both are code violations.
Troubleshooting and Resolution
Symptoms
Lights only turn on when upstairs switches are in a specific position. Fuse blew when switches were first used 30 years ago.
Diagnosis and Repair
1.
Verify Switch Types
Confirmed that all four switches are 3-way switches.2.
Identify Circuit Configuration
Determined that the circuit switches the grounded conductor (neutral) using a 3-way circuit with two switch legs (one for each light).3.
Establish Power and Neutral Connections
Connected a hot wire and neutral to the terminals on each 3-way switch where the traveler wires are normally connected.4.
Connect Light Fixtures
Connected one fixture wire to the common terminal on one 3-way switch and the other fixture wire to the common terminal on the second 3-way switch.
Result: Lights now switch independently from either the top or bottom of the stairs. Electrical code violations (switching grounded conductor and hot lamp socket screw shell) were eliminated. Flag for review