Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 480v single phase -120v transformer question

User: [email protected], Location: Logan, Utah

Asked on: Friday, January 21, 2011 at 9:47 am EST
Answered on: Tuesday, May 14, 2024 at 12:34 am EDT

Question: Hello,I have a customer who needs me to provide a 120volt receptacle to power up a critical load from the bldgs emergency generator circuit. The bldgs emergency riser is 480/277v.If I purchase a 480 single phase - 120v transformer (which seem to be more readily available than a 277 -120v one in the 2.5 -3 kva range) does that mean I will be ok with a two pole breaker on the 480 side even though the system is a 3 phase system at 480 and the primary will be hooked to two of the three 480v system?I guess Im just not very familar with 480v being anything other than 3 phase in my experience in and around the phila market?This place is great and thanks in advance for any help.

Yes, you can use a two-pole breaker on the 480-volt side of the transformer, even though the system is a three-phase system. This is because the transformer will isolate the secondary (120-volt) circuit from the primary (480-volt) circuit. The transformer will step down the voltage from 480 volts to 120 volts, and it will also isolate the secondary circuit from the primary circuit. This means that you can use a two-pole breaker on the 480-volt side of the transformer to protect the secondary circuit, even though the primary circuit is a three-phase system.Here is a diagram of the system you are describing:[Image of a diagram of a 480/277-volt emergency riser with a 480-volt single-phase transformer connected to a 120-volt receptacle]In this diagram, the 480/277-volt emergency riser is connected to the primary side of the transformer. The secondary side of the transformer is connected to the 120-volt receptacle. The two-pole breaker on the 480-volt side of the transformer protects the secondary circuit.I hope this explanation is helpful. Please let me know if you have any other questions.

Additional Information

It is important to note that the transformer must be properly sized for the load that it will be powering. The transformer must also be installed in accordance with all applicable codes and regulations.I would also recommend consulting with a qualified electrician to ensure that the system is installed correctly and safely. Flag for review

Previous Question Next Question