Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MC HL cable in Class 1 Div 1

User: MichaelJ, Location: Georgia

Asked on: Friday, January 21, 2011 at 10:00 am EST
Answered on: Tuesday, May 14, 2024 at 12:34 am EDT

Question: Situation: In a Class 1 Div 1 Area, Motors conected with MC HL cable going to motor control cabinet out side in nonhazardous area about 30' away, no junction boxes. I am sure a boubdary seal is required but is a seal required at the motors?

Yes, a seal is required at the motors.

According to NEC Article 501.15(B)(1), a suitable seal shall be provided between the Class I, Division 1 (hazardous) location and the Class I, Division 2 (non-hazardous) location. This seal shall be installed in a manner to prevent the passage of gases or vapors from the hazardous (Class I, Division 1) location into the non-hazardous (Class I, Division 2) location.In this case, the motors are located in a Class I, Division 1 area, and the motor control cabinet is located in a non-hazardous area. Therefore, a seal is required at the motors to prevent the passage of gases or vapors from the hazardous area into the non-hazardous area.

Additional Considerations: The seal should be listed for use in Class I, Division 1 hazardous locations. The seal should be installed in accordance with the manufacturer's instructions.* The seal should be inspected and maintained regularly to ensure that it remains effective. Flag for review

Previous Question Next Question