User: Dang old king, Location: Massachusetts
Asked on: Friday, January 21, 2011 at 12:18 pm EST
Answered on: Tuesday, May 14, 2024 at 12:35 am EDT
Question: Hollow: empty space ,void50kva transformers and smaller are allowed in such areas.Why 50kva limitation? Because the buildup of heat in such an unventilated area on higher rated transformers may cause them to fail and burn up.Plenum: A compartment or duct to which one or more air ducts are connected and forms part of the air distribution system.Although these areas may appear similar, they are two distinctively different portions of a building. A hollow space will not communicate to an environmental air passageway and likewise.Electrical Equipment in Plenum?s: Must be of fire-resistant construction and of the ?Low Smoke Producing Type.It is my contention that above grid return air plenums are a hollow space, but should not be considered as such, as they do indeed contain something:Environmental air, The Article in 450 does not apply to transformers in environmental air, otherwise we would allow transformers to be installed in metal ducted plenums which are void and empty as defined by the term hollow. All equipment installed in return air above grid plenums must be rated for this purpose, not just electrical equipment.Stalcup address it http://books.google.com/books?id=OkwGeMAXJa8C&pg=SA8-PA3&lpg=SA8-PA3&dq=transformers+installed+in+hollow+space&source=bl&ots=VGF24WbJ0T&sig=IoUrdqThUEkFw09h5QPHYlK5Vgk&hl=en#v=onepage&q=transformers%20installed%20in%20hollow%20space&f=falseMike Holt address it http://forums.mikeholt.com/archive/index.php/t-120884.html?The accessibility requirements prescribed in 450-13 are just that a matter of accessibility. If the hollow space communicates with and environmental air passageway, that hollow space now becomes an approved form of duct work as prescribed in the 03 International Mechanical Code. Which also address the installation of electrical equipment in environmental air return plenums in article 602.2.1.1 and then again in article 602.2.1.4 Article 300.22 applies to electrical equipment installed in environmental air plenums. The code writers intent in article 450.13 was to limit the size of a transformer based on its ability to dissipate the unwanted heat associated with transformers in concealed non ventilated space?s. Not to allow the installation of a piece of equipment in return air plenums. Although 300.22(C)2 address such applications and requirements.U/L and the President of IAEI has made information available to me ?Transformers are not tested for the plenum rating as the body of the code already address their approved installation in a hollow space up to 50kva? .Herein lies the problem.I think he,the head state inspector & my supervisor's are wrong with aligning them selves with this line of thinking.Am I wrong?Should we be allowing transformers in environmental air plenums knowing that such equipment has not or ever been tested for such an installation?
Issue
Whether transformers above 50kVA can be installed in environmental air plenums above grid return air.
Arguments
Stalcup and Holt's View
Transformers in environmental air plenums should not be considered as in a hollow space since the plenums contain air. Therefore, transformers above 50kVA could be installed in such plenums if they meet the fire-resistant and low smoke-producing requirements of 450.23.
Your View
Transformers above 50kVA should not be allowed in environmental air plenums because they have not been tested for such installations. The 50kVA limitation in 450.13 was intended to address heat dissipation in unventilated areas, not to approve transformer installation in return air plenums.
Code Requirements
NEC 450.13
Transformers above 50kVA must be installed in a location with adequate ventilation.
NEC 450.23
Electrical equipment in plenums must be fire-resistant and low smoke-producing.*
NEC 300.22(C)(2)
Transformers installed in air-handling spaces must be listed for such use.
Discussion
While Stalcup and Holt's argument has some validity, it does not fully address the issue of testing and safety. Transformers that are not specifically listed for installation in air-handling spaces have not undergone the necessary safety evaluations to ensure their performance and reliability in such environments.The NEC requires listed equipment for specific applications to ensure a minimum level of safety. Transformers above 50kVA are not typically listed for installation in air-handling spaces, and allowing such installations could create a potential hazard.
Conclusion
In accordance with the NEC and the lack of testing for transformers above 50kVA in environmental air plenums, it is prudent to adhere to the 50kVA limitation in 450.13. While fire resistance and low smoke production are important factors, they do not substitute for proper testing and listing for specific applications.
Therefore, you are not wrong to question the allowance of transformers above 50kVA in environmental air plenums. Flag for review