User: antigfk
Asked on: Friday, January 21, 2011 at 12:26 pm EST
Answered on: Tuesday, May 14, 2024 at 12:35 am EDT
Question: Based of 2008 NEC:It is my interpretation that article 590 allows the use of flexible single-conductor cable without attachment plugs for temporary, emergency situations. If I use a single-conductor #4/0awg type-W cable per phase on a 480V system, and terminate both ends using 75 degree C lugs to a circuit breaker, wouldn't the ampacity of the circuit be limited to 230A? It is my understanding, that per the requirements of 110.14(c) that the ampacity of the termination would be limited to the 75 degree C column for #4/0awg from table 310.16 (which is 230A), even the the ampacity of the cable itself is rated 405A per table 400.5(b). Is this correct?Thank you
Yes, your interpretation is correct.According to Article 590.4(B) of the 2008 NEC, flexible single-conductor cables without attachment plugs can be used in temporary and emergency situations. However, the ampacity of the circuit must be limited to the ampacity of the termination, not the ampacity of the cable.In this case, the termination is a 75-degree C lug. According to Table 310.16, the ampacity of a 4/0 AWG copper conductor with a 75-degree C insulation is 230A. Therefore, the ampacity of the circuit would be limited to 230A, even though the ampacity of the cable itself is 405A. Flag for review