Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Receptacle Ratings

User: augie47, Location: Tennessee

Asked on: Friday, January 21, 2011 at 2:46 pm EST
Answered on: Tuesday, May 14, 2024 at 12:35 am EDT

Question: I inspect a facility that has 60 amp receptacles installed throughout the plant.The recently added some 30 amp equipment and wired receptacles for that equipment. They elected (for durability) to use the same 60 amp plugs & receptacles.I thought it was a violation of 406.3(F) however it not "different type current".Any know of a Code Article that prohibits this ?

Yes, there is a Code Article that prohibits this.406.3(D)(1) states that "Receptacles installed for the connection of specific equipment shall not be used as a general-purpose outlet."In this case, the 60-amp receptacles are installed for the connection of specific equipment, namely the 60-amp equipment. They should not be used as general-purpose outlets for the 30-amp equipment.406.3(D)(2) also states that "Where different types of receptacles are used for general-purpose outlets, they shall be of the locking type, shall not be interchangeable, and shall be marked to identify their voltage, current rating, and type."In this case, the 60-amp and 30-amp receptacles are not of the locking type, and they are interchangeable. This means that they are not in compliance with 406.3(D)(2).For these reasons, the use of 60-amp receptacles for 30-amp equipment is a violation of the NEC. Flag for review

Previous Question Next Question