Topic: Reduced neutral line to industrial machine

User: collins, Location: Illinois

Asked on: Friday, January 21, 2011 at 4:00 pm EST
Answered on: Tuesday, May 14, 2024 at 12:36 am EDT

Question: I have a power enclosure with a 208/120V input. The pumps are 208v 3ph and require 200amps.The 120V is tapped off of the 3 hot legs to power a 24vdc power supply and 2 heaters. The power supply draws 3amps and each heater draws 10amps.Is there a section of the NEC that allows for a reduced neutral drop to the machine or does it need to match the 3 hot legs at 4/0?

NEC Section 215.2 Neutral Conductor allows for a reduced neutral conductor size in certain installations.

In this case, the conditions for a reduced neutral are met

The unbalanced load is less than 200 amps. (200 amps - 3 amps = 197 amps) The system is a 3-phase, 4-wire system. The neutral conductor is not carrying any unbalanced current. (Heaters and power supply are single-phase loads)

Therefore, a reduced neutral conductor size is permitted.
Reduced Neutral Conductor Sizing

The minimum size of the reduced neutral conductor is 1/2 the size of the phase conductors. (4/0 / 2 = 2/0)

Conclusion:


The NEC allows for a reduced neutral conductor size of 2/0 for this power enclosure. Flag for review