Topic: Temporary Generator Install

User: joebell, Location: New Hampshire

Asked on: Friday, January 21, 2011 at 5:18 pm EST
Answered on: Tuesday, May 14, 2024 at 12:36 am EDT

Question: Got a call from a co worker today regarding a temp gen install at a customers facility. It seems that it is not a SDS but no grounded or EGC were installed from the generator to the panel or disco it is feeding in the facility. My coworker was told by the on site engineer that it was not required. He says the neutral conductor from the premises wiring will clear a fault if one were to occur.My question is how is the fault current going to get back to the source (generator) if there was a fault with no neutral or EGC from the generator. The way I see it the only way any fault would clear is if it were phase to phase.

Without an EGC (Equipment Grounding Conductor) or a grounded neutral conductor, a fault current in the facility will not be able to return to the generator. This is because the only path for the fault current would be through the impedance of the wiring back to the generator, which is typically too high to allow for a significant current to flow.As a result, the fault current will not be able to clear, and the result will be an ongoing electrical hazard. In the event of a fault, the voltage on the faulted conductor will rise to the voltage of the generator, and this can pose a serious shock hazard to anyone who comes into contact with it.

The on-site engineer is incorrect in saying that the neutral conductor from the premises wiring will clear a fault if one were to occur. The neutral conductor is not designed to carry fault current, and it is not capable of clearing a fault. In fact, if a fault occurs on the neutral conductor, it can actually cause the voltage on the other conductors to rise, making the situation even more dangerous.

It is essential that an EGC be installed between the generator and the panel or disco that it is feeding. The EGC provides a low-impedance path for the fault current to return to the generator, and this allows the fault to be cleared quickly and safely. Flag for review