Question: We were called out to a school where a Air handler disconnect had started melting. This is actually the 2nd disconnect that had this problem. Here are the facts. There is #6 wire ran to J-box, then changes to #8 wire thhn to disconnect then down to furnace unit. The furncace unit has 10kva heat strips. The max fuse rating is 60amps. It operates on one leg being 120v and a high leg around 200v. So 240v air handler. I know that #8 is good for 50 amps if using the 75 degree column for the terminals. There were 60 amp fuses in disconnect. Would the smaller wire have caused the fire.Also when the maintence man pulled out the pull out on disconnect on of the stab blades from pull out was left in the disconnect because it was melted off. So one leg still connecting possibly.So my question is what could have caused the fire. It was cold that morning around freezing. The first disconnet that had this problem I replaced last year, I just diagonsed the issue as loose terminals. This year it was fine no sign of melting. So what could be the problem. This installation was about 7 years ago.
Possible Causes of the Fire
Overheating due to loose connections
Both #6 and #8 THHN wire can handle 55 amps if the terminals are properly torqued and maintained. Loose connections can create high resistance points, leading to overheating and melting of the wire and terminals.
Incorrect fuse rating
The disconnect should have been equipped with fuses rated for 50 amps, not 60 amps. Oversized fuses allow more current than the wire can handle, increasing the risk of overheating.
Broken stab blade
A broken stab blade could have left one leg of the circuit still connected, causing a continuous draw of current through the #8 THHN wire. This could have led to overheating and melting of the wire and disconnect.
Defective disconnect
A manufacturing defect or previous damage to the disconnect could have caused it to overheat abnormally.
Other Considerations
Cold temperatures
Lower temperatures can increase the resistance of electrical circuits, potentially aggravating any existing loose connections or other issues.
Previous issue
The fact that a previous disconnect had similar problems suggests a systemic issue, such as improper installation or maintenance practices.
Recommendations: Inspect all electrical connections in the air handler system, including the remaining disconnect, to ensure proper tightness. Replace the faulty disconnect with a new one rated for the correct amperage. Use the proper wire gauge for the circuit and install it in accordance with electrical codes. Regularly inspect and maintain electrical components to prevent similar issues in the future.* Investigate the cause of the previous disconnect failure and take corrective action to prevent recurrence. Flag for review