Question: found at a friends house a new 200 amp sq d homeline panel installed that wont trip breakers that are grounded . outlets show open grounds . do i need to run a ground wire . they didnt do it when they installed the new box , said something about the meter on the other side of the wall . anyway im trying to help her resolve this so she is safe with her kids there .would apreciate some right direction
Safety First
Shut off all power to the panel before performing any work.
Troubleshooting Steps
1. Confirm Grounding System
The panel is connected to the grounding electrode system (GES), which typically includes a grounding rod driven into the earth. Verify that the panel is properly bonded to the GES.
2. Inspect Neutral Wiring
Ensure that the white neutral wires are properly connected to the neutral busbar in the panel. Loose or incorrect connections can cause open grounds.
3. Check Grounding Wire
If the panel is not grounded, it will need a grounding wire run from the panel to the GES. The grounding wire should be bare copper or insulated green wire with a minimum wire size of #8 AWG.
4. Inspect Outlets and Devices
Remove the faceplates from the outlets and switches that are showing open grounds. Check for loose or disconnected ground wires. If necessary, tighten or repair the ground connections.
5. Test Breakers
Once the grounding issue is resolved, test the breakers to ensure they are tripping properly. Use a ground fault circuit interrupter (GFCI) tester to check for ground faults.
Additional Considerations
Meter Bonding
If the meter is on the other side of the wall, there should be a bonding jumper between the meter enclosure and the panel. This jumper provides a path for the grounding current.
Professional Electrician: If you are not comfortable performing these tasks yourself, it is highly recommended to contact a licensed electrician to ensure the safety and functionality of the electrical system. Flag for review