Topic: After GFI: connect Neutral to GND on ungrounded circuit ?

User: justdavemamm, Location: Rochester NY

Asked on: Sunday, January 23, 2011 at 10:25 am EST
Answered on: Tuesday, May 14, 2024 at 12:39 am EDT

Question: Listening to home DIY advice show on a local radio station this Sunday morning. (Rochester NY - 2008 code IIRC)The guest electrician takes a call about installing a GFI on a two wire (ungrounded) circuit. At first he says that the GFI will generate a ground. Then he says that the circuit, after the GFI, feeding an outlet recept. that has a ground hole, you are permitted to connect the neutral to the ground terminal on the recept.. That this is the only case where this is allowed.No mention of placing a sticker on the downstream indicating that it is ungrounded, or fed from a GFI.Right or wrong ? I was under the impression that it was NEVER ok to jumper the ground to the neutral there. Is there an exception for GFI's?

Wrong.

It is never permitted to connect the neutral to the ground terminal on a receptacle, even if the circuit is fed from a GFI.The electrician's statement is incorrect and violates the National Electrical Code (NEC): NEC 250.4(A)(5): "Equipment grounding conductors shall not be connected to grounded neutral conductors." NEC 404.4(A): "No equipment grounding conductor shall be connected to the neutral conductor on the load side of a GFCI."Why is this important?

Connecting the neutral to the ground can create a hazardous ground fault. If the neutral becomes disconnected downstream of the GFI, the receptacle will appear to be grounded, but it will not provide proper grounding protection. This can lead to electrical shock or fire.

Proper Installation

To properly install a GFI on an ungrounded circuit, follow these steps:1. Identify the Circuit

Ensure that the circuit is not grounded.2.

Install the GFI

Connect the LINE wires (black and white) to the appropriate terminals on the GFI.3.

Install the Outlet

Use an outlet that does not have a ground hole.

Labeling


The National Electrical Code (NEC) requires that you label any outlet that is not grounded or that is fed from a GFI. The label should clearly state: "No Equipment Ground" "GFCI Protected"This label is important because it alerts users that the outlet is not properly grounded and that it is protected by a GFI. Flag for review