Question: I am wanting to know how you would size a neutral to a sub panel that you are installing for 3phase loads only. I know the code says to run a neutral also, But how do you come up with the correct size. The feeder I am running is a 200A 3phase. I am running 3-3/0 thhn for L1,L2, L3 and a #6 EGC. Any help would be appreciated.
Method 1: 2.5% of Line CurrentStep 1: Calculate the line current.
Line current = Phase current = Phase voltage / ImpedanceAssuming 3-phase, 480V service, the line current will be the same for each phase.Phase voltage = 480V / 1.732 = 277VImpedance = 3/0 THHN copper conductor: 0.103 ohms/1000 ftLet's assume a 50-foot run, so impedance = 0.103 ohms (50 ft / 1000 ft) = 0.0052 ohmsPhase current = 277V / 0.0052 ohms = 53,269 ampsStep 2: Calculate the neutral current.
Neutral current = 2.5% of line currentNeutral current = 0.025 53,269 amps = 1,331.73 ampsStep 3: Size the neutral conductor.
Based on the calculated neutral current, the neutral conductor should be:#4 THHN copper conductorMethod 2: Sum of Unbalanced Load CurrentsStep 1: Determine the unbalanced load currents.
In a 3-phase system, the unbalanced load currents are the differences between the line currents.Let's assume that the load is unbalanced by a factor of 10%:Unbalanced load current on L1 = 10% of line current = 0.1 * 53,269 amps = 5,327 ampsUnbalanced load current on L2 = 0 amps (no unbalanced current)Unbalanced load current on L3 = 5,327 ampsStep 2: Calculate the neutral current.
Neutral current = Sum of unbalanced load currentsNeutral current = 5,327 amps + 0 amps + 5,327 amps = 10,654 ampsStep 3: Size the neutral conductor.
Based on the calculated neutral current, the neutral conductor should be:#3 THHN copper conductorRecommendation:
Since Method 2 yields a larger neutral conductor size, it is recommended to use a #3 THHN copper conductor as the neutral. Flag for review