User: wmeek, Location: Texas
Asked on: Sunday, January 23, 2011 at 4:36 pm EST
Answered on: Tuesday, May 14, 2024 at 12:39 am EDT
Question: If you were to run a 2" conduit into the side of a gutter or a Pull Box and leave it via the back of the box, would you size it to 6X the diameter of the conduit. If so would a 12"x12"x4" pull box work . Per 312-6(A)
Yes, if you were to run a 2" conduit into the side of a gutter or a Pull Box and leave it via the back of the box, you would size it to 6X the diameter of the conduit.
According to NEC 312-6(A)
"Conductors entering a raceway shall be protected by one of the following means:(1) Entering a chase, pull box, junction box, or other enclosure that is provided with a separately accessible cover that can be removed for the examination or servicing of the conductors or their connections."
Sizing the Pull Box
The diameter of the conduit is 2", so the minimum pull box size would be 6 x 2" = 12". However, the pull box must also accommodate the conductors inside the conduit, which is not specified in the question.
Based on the given dimensions:
A 12"x12"x4" pull box has a rectangular cross-section with an area of 144 square inches. This size may be suitable if there are only a few conductors in the conduit. However, if there are a large number of conductors, a larger pull box may be required.Therefore, while the dimensions of the pull box you mentioned (12"x12"x4") meet the minimum requirements of 312-6(A), it may not be sufficient for your specific application. You should determine the number and size of conductors in the conduit and consult the applicable electrical codes and standards to select an appropriately sized pull box. Flag for review