Topic: 400A Service

User: wmeek, Location: Texas

Asked on: Sunday, January 23, 2011 at 9:45 pm EST
Answered on: Tuesday, May 14, 2024 at 12:40 am EDT

Question: I have a 3" rigid riser with 3-#500mcm and 1-#350(neutral) line side of a 320 metercan,. On the load side I have two sets of 3/0 going to to two 200A Disconnects. Is this code compliant for a 400A Service as long as the calculated load does not exceed 380A.

Yes, as long as the calculated load does not exceed 380A, this configuration is code compliant for a 400A service.

Conduit Sizing

The 3" rigid riser is sufficient to accommodate the number and size of conductors per NEC Table 310.16: 3-#500mcm + 1-#350 = 4 x 1.028 sq in = 4.112 sq in 3" conduit = 7.068 sq in 4.112 / 7.068 = 58% fill, which is below the maximum of 75% per code.

Current-Carrying Capacity

The 3-#500mcm conductors are rated for 200A each per NEC Table 310.16. The 1-#350 neutral conductor is rated for 175A per NEC Table 310.16. The total current-carrying capacity of the line side conductors is 3 x 200A + 175A = 775A. The load side conductors (two sets of 3/0) are rated for 200A each per NEC Table 310.16.

Load Calculation:
* Since the calculated load does not exceed 380A, which is less than the current-carrying capacity of the conductors, the system is within the code requirements. Flag for review