Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Qualitative question on sizing a circuit for a sub-panel

User: tonype, Location: New Jersey

Asked on: Monday, January 24, 2011 at 7:27 am EST
Answered on: Tuesday, May 14, 2024 at 12:40 am EDT

Question: Sub panel as the following: 40-amp 220 v for elevator; 20-amp, 220-v for kitchen range and 17, 120-v breakers (15 or 20 amps) for lighting and power.Install has a 40-amp breaker in the main panel feeding this sub. My gut tells me this is too low.My though that a minimum of 60-a is needed - am I looking at this properly?

Yes, you are correct. A 40-amp breaker is too low for this sub panel.

Load Calculation

Elevator: 40 amps (220v x 40amps = 8800 watts) Kitchen range: 20 amps (220v x 20amps = 4400 watts)* Lighting and power (17 breakers): Assume an average of 10 amps per breaker = 170 amps (10 amps x 17 breakers)

Total Load

8800 + 4400 + 1700 = 15,000 watts

Breaker Size

The minimum breaker size required is 15,000 watts / 240 volts = 62.5 amps.

Conclusion:


A 60-amp breaker is the minimum size required for this sub panel to provide safe and reliable power to the connected loads. Flag for review

Previous Question Next Question