Topic: Can Article 645 be used for Industrial Control Rooms with Raised Floor?

User: jtinge, Location: Hampton, VA

Asked on: Monday, January 24, 2011 at 11:55 am EST
Answered on: Tuesday, May 14, 2024 at 12:41 am EDT

Question: To utilize the less restrictive wiring methods of Article 645, the six criteria listed in 645.4 of NEC 2011 have to be met. Three of those are the "room contains only listed IT equipment", "occupied by and accessible to, only those personnel needed for the maintenance and functional operation of the installed information technology equipment", and "only electrical equipment and wiring associated with the operation of the information technology room is installed in the room. Can an industrial control room having a raised floor be classified as IT room and utilize the Article 645 wiring methods if it contains industrial PLCs and other equipment in addition to listed IT equipment for control of processes or a plant and is accessible to operators of that of the non-listed equipment? It seems that many people classify these control rooms as IT rooms but the equipment and personnel accessible to that equipment don't meet the criteria of Article 645 that permits use of the less restrictive wiring methods. Is this correct? Can Article 645 be correctly utilized for industrial controls rooms as described above?

Can Industrial Control Rooms be Classified as IT Rooms?

No, industrial control rooms that contain non-listed industrial equipment in addition to IT equipment cannot be classified as IT rooms under NEC Article 645.

Criteria for IT Room Classification

According to NEC 645.4, an IT room must meet all six criteria specified in the article. Three of these criteria are: The room contains only listed IT equipment. The room is occupied by and accessible to only personnel needed for maintenance and operation of the IT equipment. Only electrical equipment and wiring associated with IT equipment are installed in the room.

Industrial Control Rooms vs. IT Rooms

Industrial control rooms typically contain a mix of listed IT equipment and non-listed industrial equipment, such as PLCs and process control systems. Additionally, these rooms are often accessible to operators who are not involved in the maintenance or operation of the IT equipment.

Non-Compliance with Article 645

Since industrial control rooms do not meet the criteria of NEC 645, they cannot utilize the less restrictive wiring methods permitted under the article. These wiring methods are intended for use only in areas where there is a low risk of fire and electrical hazards, such as IT equipment rooms.

Consequences of Incorrect Classification

Incorrectly classifying an industrial control room as an IT room and using non-compliant wiring methods can pose safety and code violation risks, including:
Increased fire hazard due to improper wiring techniques. Lack of compliance with NEC requirements, which could result in fines or permit denials. Potential insurance coverage issues in the event of an electrical fire.

Conclusion:


Therefore, industrial control rooms containing both listed IT equipment and non-listed industrial equipment cannot be classified as IT rooms under NEC Article 645 and must use wiring methods that comply with other applicable code articles, such as Article 501 for flexible cords and cables. Flag for review