Topic: Proper Gutter for a service

User: wmeek, Location: Texas

Asked on: Monday, January 24, 2011 at 12:10 pm EST
Answered on: Tuesday, May 14, 2024 at 12:41 am EDT

Question: This is my scenerio: I have a 320 Meter can and i am running parallel 2" emt from meter can up to the bottom of a6x6 Gutter. Also to the left of these 2" conduits will be a 1phase 200A disconnect and a 3phase 200 amp disconnect hanging from the bottom of gutter. 1phase disconnect will have 2-3/0 , 1-2/0 , and 3phase disconnect will have 3-3/0, 1-3/0. Also in the gutter will be a 1/0GEC Bldg. steel, 1/0 Gec to water pipe and #4 to each disconnect. 1-#4 to all bonding bushings in gutter. GEC to ground rod will be ran to meter can(per Utility).6(A). I came up with a 6x6 gutter size per 366.22 and 312-6(a).My question is this code compliant installation.

Yes, the proposed installation appears to be compliant with the following code requirements

Gutter Size:
366.22 requires a gutter with a cross-sectional area sufficient for the service conductors and associated equipment. 6x6 gutter is typically acceptable for the number and size of conductors you specified.312.6(a) Clearance for Conductors Entering Equipment

Conduit bodies and enclosures utilized with conduit sizes larger than 2 inches are required to have a cross-sectional area not less than twice the cross-sectional area of the largest conduit entering the equipment. 2" EMT has an area of 3.14 square inches. Therefore, a 6x6 gutter with an area of 36 square inches meets this requirement.

Conductors and Disconnects

The 200A single-phase disconnect should have 3 conductors: 2-3/0 and 1-2/0. The 200A three-phase disconnect should have 4 conductors: 3-3/0 and 1-3/0.

Grounding

A 1/0 grounding electrode conductor (GEC) should be run from the gutter to the building steel and water pipe. A #4 GEC should be run to each disconnect. A #4 bonding conductor should be run to all bonding bushings in the gutter. A 1/0 GEC should be run from the meter can to the ground rod (per utility requirement).

Conduit Type

2" EMT is an acceptable conduit type for running the service conductors from the meter can to the gutter.

Additional Considerations:
Ensure the gutter is adequately supported and anchored to prevent damage or failure. Maintain the proper bending radius for the conductors within the gutter. Label all conductors and equipment for easy identification.* Obtain any necessary permits and inspections from the local authority having jurisdiction.It is important to note that this is a general overview of the code requirements that apply to your scenario. Always refer to the specific code sections and consult with a qualified electrician for a thorough and compliant installation. Flag for review