User: Open Neutral, Location: Inside the Beltway
Asked on: Monday, January 24, 2011 at 1:28 pm EST
Answered on: Tuesday, May 14, 2024 at 12:41 am EDT
Question: I'm trying to contrast several ways of solving a design problem, in hopes of finding the least uneconomical ones. Variables in play includes what voltage to use, where to accept the PoCo's feed and metering, and how much of the total load gets backup.I'd appreciate your estimates on some pricing; as I've thus far been quoted numbers that vary by 6-10dB...One attack would use ~15KW MV:480/208 transformers, one to go up to some MV {4160~5KV} for a 700' run, through MV cable and then then the other back down. Outdoor mounting (Does NEMA 3R apply at MV?)Another would need a big 200A 277/480V 3 ph 4 pole transfer switch vs. a 50A 208/120 one.Could you learned persons throw out your guesstimates on what such transformers and switches would go for?On the transfer switch, are there non-automatic ones; i.e. we [via a control system] decide when to change? (The term "Manual Transfer Switch" seems to imply Manny is the guy moving the switch; not what we want.)Thank you
Transformer Pricing Estimates
15 kW MV:480/208 transformer for 700' run (including MV cable): $10,000-$15,000 200 kVA MV:480/208 transformer for 700' run (including MV cable): $20,000-$25,000
Transfer Switch Pricing Estimates
200 A 277/480V 3 ph 4 pole automatic transfer switch: $5,000-$10,000 50 A 208/120V single pole automatic transfer switch: $1,000-$2,000 200 A 277/480V 3 ph 4 pole non-automatic transfer switch: Not readily available, but potentially custom-made at a higher cost.
Additional Notes: NEMA 3R enclosure rating applies to outdoor use at MV voltages, providing protection against rain, sleet, and external icing. Manual transfer switches require manual operation to switch between power sources. They may be used in certain limited applications where automatic switching is not required or desired. The cost estimates provided are approximate and may vary depending on factors such as manufacturer, features, and market conditions. Flag for review