Question: i need manuals for the simplex 2001 and the 4802 panels so i can figure out how to get an alarm signal out of them for remote monitoring by another panel...
Simplex 2001 Panel Manual Title
Simplex 4007 Advanced Addressable Fire Alarm System Installation and Operation Guide
Document Number
5003300010
Download Link
https://www.simplexgrinnell.com/catalog/getDoc?catalog=5003300010&DocType=Manual
Simplex 4802 Panel Manual Title
Simplex 4802 Fire Alarm Control Panel User Guide
Document Number
5005920060
Download Link
https://www.simplexgrinnell.com/catalog/getDoc?catalog=5005920060&DocType=Manual
Remote Monitoring Signal Wiring2001 Panel
Output Type
Form C Contact
Wire Color Code
Red (NO), Black (COM), Green (NC)
Terminals
T109, T110, T111
4802 Panel
Output Type
Form C Contact
Wire Color Code
Red (NO), Black (COM), Green (NC)
Terminals
J3-13, J3-14, J3-15
Wiring Instructions
1. Connect the NO (Red) wire to the input terminal of the remote monitoring panel.
2. Connect the COM (Black) wire to a common ground.3. Connect the NC (Green) wire to the NC terminal of the remote monitoring panel.
Additional Notes: The output contacts are rated for 2A @ 30VDC. The remote monitoring panel must be compatible with Form C contacts.* Refer to the specific user guide for your remote monitoring panel for additional configuration instructions. Flag for review