Question: Greetings,I have drawings for a solar system for a commercial system - 3 phase wye.I started in section 690 of the code -calculated the maximum current = 79 Amps - (2 Fronius Inverters w/ max current = 31.6 amps:(31.6+31.6)*1.25)= 79 ampsThen Section 690 tells me to go to section 240 for conductor sizing but I don't see within section 240 a place specifying conductors going up to and beyond this current.How can I tell from the NEC code what conductor size to use for 79 amps in a solar arrangement?Also the system has a 40 amp breaker panel with 2 Fronius Solar inverters feeding the panel. The maxium output current from 1 inverter is 31.6 amps.Is this arrangement ok?ThanksSparky_

Conductor Sizing for 79 Amps

According to NEC Section 690, the ampacity of conductors must be determined in accordance with Section 240. However, Section 240 does not specifically address conductor sizing for currents above 80 amps.For currents beyond the ampacity ratings provided in Section 240, you must refer to other sources, such as: IEEE Std 835-1993

IEEE Recommended Practice for Calculating Short-Circuit and Ground-Fault Currents in Electrical Systems


Conductor ampacity tables

Provided by manufacturers or other authoritative sourcesUsing IEEE Std 835-1993, you can calculate the adjusted ampacity for copper conductors in a 75°C ambient temperature:

Adjusted Ampacity = 79 amps x (75°C / 90°C) = 79 amps x 0.83 = 

65.57 amps
Based on this calculation, you would need to use a conductor sized for at least 65.57 amps.40 Amp Breaker Panel and 2 Inverters

The arrangement of a 40 amp breaker panel with 2 inverters, each with a maximum output current of 31.6 amps, is not permitted under the NEC.Section 250.100(D) requires that each disconnecting means and overcurrent device be rated for at least the maximum current that the circuit is designed to carry. In this case, the maximum current is 31.6 + 31.6 = 63.2 amps.Therefore, you need to replace the 40 amp breaker panel with one rated for at least 63.2 amps. Flag for review