Question: What are the stipulations for reducing the neutral conductor and is there a certain percentage that it cannot be reduced past?
Stipulations for Reducing the Neutral Conductor
Neutral Current Balance
The system must be essentially balanced, meaning that the neutral current is within 10% of the phase current.
Compliance with NEC
The reduction must comply with the requirements of the National Electrical Code (NEC) Article 220.
Specific Conditions Met
The following specific conditions must be met: A qualified electrical engineer performs a neutral current analysis. Grounded conductors serve only as neutrals. All phase conductors connected to the neutral conductor are of equal length and impedance. The reduction is made at the panelboard or switchboard where the neutral is distributed. The neutral conductor is not used for equipment grounding.*
Verification
The system must be verified to meet the reduction criteria after the reduction is made. This can be done through load measurements or the use of a neutral current transformer.
Percentage Limitation
The NEC does not specify a specific percentage limit that the neutral conductor cannot be reduced past. However, generally accepted practice is to reduce it by no more than
80% of the phase conductor size. This is because the neutral conductor is still required to carry some return current, and reducing it too much can create safety issues.
Caution:
Reducing the neutral conductor can only be done when the above stipulations are met. Failure to adhere to these stipulations can result in overheating, overloading, and potential hazards. It is recommended to consult with a qualified electrician before making any modifications to the neutral conductor. Flag for review