Asked on: Monday, January 24, 2011 at 6:16 pm EST
Answered on: Tuesday, May 14, 2024 at 12:42 am EDT
Question: Can non-electrical piping be in a cable tray?I have a outdoor open ladder style cable tray that will have tec cable of varing voltages, 24v -480 volts. For the cables i have and extra spacing i only need 18" of a 30"tray. The owner of the site would like to run his piping for infloor heat in this tray aswell. It consistes of 2 pex pipes inside 1 corragated 4" pipe. The extra space inside the large pipe is foam filled.I couldn't find any code article that won't allow this.
NEC Article 392.7(C) states that "Cable trays shall not contain any conductors other than the conductors of the electric system."ButNEC Article 392.8(A) states that "Listed cable trays and fittings shall be permitted to contain one or more communications raceways."This means that non-electrical piping is not allowed in a cable tray unless it is in a separate raceway that is listed for that purpose.In your case, the piping is not in a separate raceway, so it is not allowed in the cable tray.
Additionally, the foam filling in the pipe is a potential fire hazard and is not allowed in a cable tray.
Recommendation:
You should install a separate raceway for the piping and keep it outside of the cable tray. Flag for review