Question: I'm looking for a code referernce (If one exists) that says when you have a grounding wire run within emt that you need to bond the wire to each box.I have 3 circuits (2 different neutrals) going through various 5 inch boxes for lighting and power. All the piping is EMT.Thanks
National Electrical Code (NEC)Article 250: GroundingSection 250.148: Connection to Boxes and Fittings(D)(5) For raceways containing two or more circuits, there shall be at least one ground clamp or other listed grounding means for each raceway at every outlet box, junction box, and similar fitting where a change occurs in the direction of the raceway, or where a ground wire connects to a splice.
This code section requires that a grounding wire within an EMT raceway be bonded to each box where the raceway changes direction or where a ground wire connects to a splice. Since you have multiple circuits (with different neutrals) going through multiple 5-inch boxes, you will need to ensure that the grounding wire is properly bonded to each box.
Additional Notes: The grounding wire should be a bare solid copper conductor with a minimum size of AWG #12. The ground clamp or other grounding means should be listed and rated for the size of the raceway and the number of conductors in the raceway.* Ensure that all connections are properly made and tightened to the specified torque values. Flag for review