Topic: GFCI protection in woodwork factory.

User: Chamuit, Location: Texas

Asked on: Monday, January 24, 2011 at 11:37 pm EST
Answered on: Tuesday, May 14, 2024 at 12:43 am EDT

Question: Is GF protection required for general service receptacles in a woodworking factory? The receptacles are to be used at assembly tables.I looked through 210.8 and Commetary Table 210.1 (2005) and didn' see anything.

There is no GFCI protection required for general service receptacles in a woodworking factory, even if they are used at assembly tables, as per the 2005 NEC. Flag for review