User: jmellc, Location: Durham, NC
Asked on: Tuesday, January 25, 2011 at 8:01 am EST
Answered on: Tuesday, May 14, 2024 at 12:44 am EDT
Question: Did a job this week where original wiring was done late 1950's or early 1960's. All 2 wire receptacles. About half the cloth NM cable was grounded, half not. Customer wanted grounded receptacles all over, so we ripped the old and put in the new. Too bad for him they didn't used grounded cable all through. We could have just replaced receptacles.The grounds that were in cables were either cut out, left hanging or grounded to the box. Some boxes had a grounded & ungrounded NM cable. Some grounds were intact, some cut out, some grounded to the box.Good for me, but a shame for the customer. If all had been grounded, we could have simply changed receptacles to 3 wire. I'm sure this was the in between years, when some houses began having grounded receptacles & more cable was being made with grounds. Some of these cables had insulated grounds too. I've only seen bits & pieces of that over the years.
It is indeed unfortunate that the original wiring in your customer's house was not consistently grounded. This is likely due to the fact that during the late 1950s and early 1960s, there was a transition period during which some homes were wired with grounded receptacles and NM cable, while others were not.As you mentioned, during this time, some NM cable was manufactured with a grounded conductor, while some was not. In cases where the NM cable did not have a grounded conductor, the ground wire was often simply cut out or left hanging, or it may have been grounded to the box. This was a common practice at the time, but it is not considered to be up to code today.In order to ensure that all of the receptacles in your customer's house were properly grounded, it was necessary to replace all of the old NM cable with new cable that had a grounded conductor. While this was undoubtedly a more expensive and time-consuming project than simply replacing the receptacles, it was the safest and most code-compliant option.It is important to note that even though some of the NM cable in your customer's house had an insulated ground wire, this does not necessarily mean that the cable was properly grounded. In order for the ground wire to be effective, it must be properly connected to a ground rod or other grounding electrode. If the ground wire is not properly connected, it will not provide any protection against electrical shock.I am glad to hear that you were able to complete this project safely and successfully. It is always important to ensure that electrical work is done in accordance with the applicable codes and standards. Flag for review