Topic: Voltage labels

User: Davebones, Location: North Of Tampa Fl

Asked on: Tuesday, January 25, 2011 at 8:03 am EST
Answered on: Tuesday, May 14, 2024 at 12:44 am EDT

Question: We have controllers that have two sources of power into them 120V and 480V . We have them labeled with 480V labels ( black letters orange background ) . We have a label on the front saying " Caution Two Sources Of Power " . Do we also need another label with 120V on them ?

Yes, it is recommended to have a separate label indicating the presence of 120V in addition to the 480V label.According to NFPA 70E: Standard for Electrical Safety in the Workplace, any electrical equipment that has multiple voltage sources should be clearly labeled to indicate the voltage range and the source of each voltage.The purpose of these labels is to provide clear and concise information to qualified electrical workers about the potential hazards associated with the equipment. By having a 120V label, it helps to ensure that workers are aware of the potential for both 480V and 120V, reducing the risk of electrical accidents and injuries. Flag for review