Topic: Installing GEC conductors without a Gutter

User: wmeek, Location: Texas

Asked on: Tuesday, January 25, 2011 at 8:25 am EST
Answered on: Tuesday, May 14, 2024 at 12:44 am EDT

Question: I am installing a 400A Service using 320 Metercan and coming off the load side of meter can with 2-2" conduits to two 200A disconnects. My question is can I install a J-box and run Bldg steel, water pipe GEC's to a ground bar in j-box and then run #4 to each disconnect to bond the service disconnects. My GEC to ground rod will take place at the meter can per PoCo. All my conductors will be ran exposed( Unless code prohibits). If anyone has a photo of this type of installation and could post it that would be very helpful. The disconnects dont have the required space to make these connections. I do not know how to add pictures on this site.

Yes, you can install a J-box and run grounding electrode conductors (GECs) from the building steel, water pipe, and ground rod to a ground bar in the J-box. From there, you can run #4 conductors to each disconnect to bond them together.

Here is a diagram of how the system should be installed

[Image of a diagram showing the installation of a J-box for bonding service disconnects]

The following steps outline how to install the system

1. Install a J-box on the outside of the building, near the service entrance.
2. Run the following GECs to the ground bar in the J-box: A #4 copper conductor from the building steel A #4 copper conductor from the water pipe A #6 copper conductor from the ground rod3. Connect each GEC to the ground bar using a ground lug.
4. Run a #4 copper conductor from the ground bar to each service disconnect.5. Connect the #4 conductor to the grounding terminal on each disconnect.


Note that the following code requirements must be met

The GECs must be sized in accordance with Table 250.66 of the National Electrical Code (NEC). The ground bar must be sized in accordance with Table 250.28(A) of the NEC. The #4 conductors that bond the service disconnects together must be run in a raceway.

I do not have a photo of this type of installation, but I hope the diagram and instructions are helpful.